220 outlet
  • basshnter1
    • Jul 2003
    220 outlet
    my moms heat pump went out this week.
    we have decided to temporarily install a window unit in the kitchen
    window where there was one before the heat pump was installed.
    there is no voltage on the 220 outlet.
    I checked the breakers and there isnt one labled window ac anymore
    like I remember but all the breakers are on.
    there are no extra spaces in the box to add a breaker and all are being used.
    I removed the panel cover(I didnt touch anything inside!) and saw one
    red and one black wire just hanging there not connected to anything.
    Could this be to the 220 outlet.
    The heat pump was added years after the house was built so is it
    possible the heat pump contactor used the old window ac breaker to
    supply the heat pump because there was no space in the panel?
    Is there a safe way for me to check continuity from the red&black wire
    s in the panel to the 220 outlet.
    thanks in advance. rick
  • handyandy
    • Sep 2002
    • 209
    Sounds to me like that is exactly what happened, he used the 220 volt for the heat pump. You should be able check the line with a continuity tester, as long as the continuity tester has a way to send current.
    • basshnter1
      • Jul 2003
      I turned off main power to panel (checked with voltmeter).I removed the two wires from the
      220 breaker labeled, heat pump ac compressor and wired up my black&
      red wires in the panel and the window unit fired right up.
      The breaker I used was the one previously used for this 220 outlet.
      thanks for this board, rick.
      • handyandy
        • Sep 2002
        • 209
        Glad you got it worked out. Now you can help us with your experiences. Welcome to the forum!