Recently purchased an old home (1941) in Virginia. My home inspector missed that my outside service was only to code for 50amps while my circuit breaker was set for 100amps. An electrician has told me the work is significant to upgrade to 100amps to be to code and is in the range of $800 to repair or could upgrade to 200amps for $1200. Is the first most likely necessary? And is the price of either bringing up to code or upgrading reasonable?
Upgrading Cable and Meter for service
Tags: None
The National Electrical Code established that the absolute minimum for residential service entrances is 100 amperes.
The figures you gave $800 and $1200 respectivbely for a 100 and 200 is just about right.
Materials for a 100 amp typically run about $325 for the panelbox, $18 for the meter socket, $12 for the weatherproof connector, $5.25 for the weatherhead etc.
The cable size is 2/3 aluminum SEU for 100 and 4/0-3 for a 200 amp and I've seen prices from $1.88 to 2.03 per foot.
The "Cadillac" of entrance panels can cost considerably more - Cutler-Hammer, Square "D" some Siemens panels and all panels with bolt in circuit breakers.
Mind you in changing out panels, the new code says you have to protect all bedroom circuits with arc-fault breakers. This started in Jan 1 2001.
Initially they were expensive but have come down drastically in price while maintaining their protection factor.