gfci -- Need suggestions/Help
  • vankemp
    • Aug 2007
    Several weeks ago I lost power to several of my kitchen outlets. I have tried and failed to diagnose the problem on several occasions. Below I explain my attempts...
    Of the outlets not working, Refer (non-gfci outlet) and two other kitchen outlets that are gfci outlets.
    First attemp was checking all breakers, including any other possible gfci that might be on same line---none was tripped. I then replaced 2 of the gfci outlets---still nothing. I tested the breakers and I do have power to the outlets.
    I have the outlets wired with the line wires (those from the box) to the "line" hook up of the gfci. Still nothing. I have tried to reset the gfci, still no luck.
    Can someone explain how the "load" portion of the gfci works? Is it possible that if it is another outlet that is not working could cause this? For example: I have power at the gfci line in, but if the load is going to another outlet that is faulty, would this break the circuit?
    I have a feeling this is something very simple, and that is the reason for the post...
    Thanks in advance,
    VK
  • vankemp
    • Aug 2007
    Figured it out
    It was both a faulty gfci AND a short on another outlet that was on same circuit---Took some time and tracing of circuits, but I got it!
    VK
    • 596
      • Jul 2007
      • 90
      Thank you for posting back with your success. That was an unusual problem, and we would have been hard pressed to diagnose it sight unseen.