    washer / gas dryer electrical requirement

    Iwant to install a washer and gas dryer.
    My question is, do I need a designated circuit?
    If so do I need a designated circuit for both, or can I run them both off of the same outlet?
    Do I use 12-2 or 14-2...15 amp or 20amp?
  • Java_Bob
    Handyman
    • Sep 2006
    • 168

    #2
    you can run both off a dedicated 20 amp, #12 awg
    Is it beer thirty??

    Comment

    • ryandebny
      Handyman
      • Jan 2008
      • 37

      #3
      Thanks

      Thanks...saved me a head ache.
      Not beer thirty...half past draft

      Comment

      • spotty
        New Member
        • Mar 2008
        • 11

        #4
        I typicaly run a 12-3 and use two seperate receptacles

        Comment

        • HayZee518
          Deity

          • Jul 2004
          • 8746

          #5
          spotty - the 12/3 with a common neutral is ok as long as your breaker feeding the receptacles is a two pole common trip. Two single pole breakers would not do as when you kill one circuit the other is still hot!

          Comment

          • spotty
            New Member
            • Mar 2008
            • 11

            #6
            Yes I know, I am a journeyman electrian, I guess I should have stated that in how I would install it. Sometimes I think people just know but thats not always the case. Sorry for my unclarity. At least these two outlets don't have to be GFI or AFCI protected, But do they have to tamperproof....probally I believe all 15 and 20 recepticles are supposed to be.

            Comment

            • HayZee518
              Deity

              • Jul 2004
              • 8746

              #7
              what do you mean "tamperproof?"

              Comment

              • spotty
                New Member
                • Mar 2008
                • 11

                #8
                2008 NEC article 406.11 Tamper resistant recepticles in dwelling units. In all areas specified in 210.52, all 125 volt 15,and 20 amp receptacles shall be listed tamper-resistant recepticales.

                Comment

                • Speedy Petey
                  Apprentice
                  • Nov 2006
                  • 214

                  #9
                  Originally posted by spotty
                  I typicaly run a 12-3 and use two seperate receptacles
                  May I ask why? Both a washer and gas dryer are perfectly fine on a shared 20A circuit.


                  Originally posted by spotty
                  At least these two outlets don't have to be GFI or AFCI protected,
                  They absolutely DO need GFI protection IF they are within 6' of a laundry sink.


                  Tamper-proof ONLY applies to areas who have adopted the 2008 NEC with no amendments for that section.
                  NOT nearly every place has.

                  Comment

                  • spotty
                    New Member
                    • Mar 2008
                    • 11

                    #10
                    Originally posted by Speedy Petey
                    May I ask why? Both a washer and gas dryer are perfectly fine on a shared 20A circuit.
                    It's the way the contractor I worked did things now it's just habbit

                    Comment

                    • spotty
                      New Member
                      • Mar 2008
                      • 11

                      #11
                      how many people have a wet sink within six ft of the outlet, and a motor on a gfi circuit can become a nuciance trip.

                      Comment

                      • spotty
                        New Member
                        • Mar 2008
                        • 11

                        #12
                        Originally posted by Speedy Petey
                        Tamper-proof ONLY applies to areas who have adopted the 2008 NEC with no amendments for that section.
                        NOT nearly every place has.
                        Might as well adopt to the code. It probally won't go into full affect until next code cycle but it's in there, and supply houses are already stocking them.

                        Comment

                        • Speedy Petey
                          Apprentice
                          • Nov 2006
                          • 214

                          #13
                          Originally posted by spotty
                          Might as well adopt to the code. It probally won't go into full affect until next code cycle but it's in there, and supply houses are already stocking them.
                          NOT mine.
                          If my customers want them I'll certainly install them, but they'll pay for it. It's for damn certain I will not bid them into a job. Wanna know why??? Because NO ONE else around here is either.
                          Same goes for AFCIs all over. My area does not require them so they don't go in unless I am asked to.

                          I DO NOT buy into the theory that "Well, it'll be code eventually so why not do it." mentality.

                          Comment

                          • Speedy Petey
                            Apprentice
                            • Nov 2006
                            • 214

                            #14
                            Originally posted by spotty
                            how many people have a wet sink within six ft of the outlet,
                            Ummm, a lot! I have a laundry sink RIGHT next to my washer.

                            I suggest you read 210.8(A)(7).
                            In fact I'll post it for you:

                            210.8 Ground-Fault Circuit-Interrupter Protection for Personnel

                            (A) Dwelling Units
                            All 125-volt, single-phase, 15- and 20-ampere receptacles installed in the locations specified in (1) through (8) shall have ground-fault circuit-interrupter protection for personnel.

                            (7) Laundry, utility, and wet bar sinks — where the receptacles are installed within 1.8 m (6 ft) of the outside edge of the sink



                            NO ifs ands buts OR exceptions. GFI protection IS required even if the receptacle is behind the washer or dryer.




                            Originally posted by spotty
                            and a motor on a gfi circuit can become a nuciance trip.
                            So what.

                            Comment

                            • jnaas2
                              Apprentice
                              • Feb 2008
                              • 213

                              #15
                              You guys may want to point out to people who are not familar with electricity that you can run 2 seperate circuits on a 12/3 with ground but that you need to make sure that you dont connect to the same phase since your neutral wire sees the current from a unbalanced circuit. If you connect your hot wires to the same phase the neutral wire will carry the the current that the 2 hot wires are carrying and if you lose the neutral wire it turns a parallel circuit into a series circuit and can smoke appliances that are being used on that circuit.