I am adding a subpanel next to my main breaker panel to allow for more circuits. We have been splitting each room off onto separate circuits as we remodel rooms hence the need for a sub-panel. I am using a Siemens 125A main lug panel as the sub connected to the main panel with #6 Stranded Copper THHN. I need a clarification on what is the max amperage for #6 stranded copper THHN? I have seen it rated both at 60A and 75A.
Announcement
Collapse
No announcement yet.
Max Amperage for #6 Copper THHN
Collapse
Forum Top GA Ad Widget
Collapse
X
-
depends at the temperature rating you're using is. in conduit I would use the lower temperature rating. four conductors within a raceway. two hots, one neutral and one equipment ground. the neutral will not be bonded to the case ground. the equipment ground will be connected to the enclosure ground [in intimate contact with the enclosure]
-
between the main panel and the sub panel needs to be four conductors - be it right next to - or 200 feet beyond the main panel. sub panel breaker sizing is 60 or 65 amp no bigger. Neutral is isolated "above ground" no green bonding screw. Aux ground - bare #6 connects here. All romex grounds go here. All white neutrals go here. Hots go to respective breakers. New construction - new bedrooms - all power receptacles need arc fault breakers feeding these circuits. [check with your local inspecting authority to se if they require it] - NEC says yes, they might be different.
Comment
-
ok, if you look in a type AC cable, you'll see a green conductor. this goes to the aux ground strip. regular bx cable just has the cable sheath as the equipment ground. a green equipment ground is pulled in with the conductors and neutral in emt conduit. in normal cases and good tight fittings a ground is not needed but sloppy or in adaquate connections a pulled ground is almost always needed. screw connectors qualify here. compression connectors do not. rigid connections do not.
Comment
Comment