I am looking for circuit breaker size for ge jb640srss cook stove....it was installed 2 months ago and tonight it tripped the breaker.......the circuit breaker is 30 amp I thought hat seemed small...it has high dollar floor so I didn't want to mess up floor looking for amp rating unless I had no other way out...this info is not in the manual
Announcement
Collapse
No announcement yet.
ge jb640srss tripped circuit breaker
Collapse
Forum Top GA Ad Widget
Collapse
X
-
am looking for circuit breaker size for ge jb640srss cook stove.
JFYI
Dan O.
Appliance411.com
The Appliance Information Site
=D~~~~~~
.
-
Range Breaker
"Quick Specs" say use a 40 amp breaker for a 10.5 Kw range BUT
if you calculate it out 10,500 divided by 240 equals 43.75 amps -- more than a double 40 will hold.
Pigtails for ranges are four wire, 50 amp. Hard wired - don't matter watts is watts.
Go with a #6-4 cable and use a 50 amp two pole breaker.
If your contractor wired it with No 10 he ought to go back to school.
any range a minimum of 6-4 copper.
Jenn-air are usually rated higher - say, 60 amp two pole.