I am attempting to hook up two 18000 btu air conditioners to one breaker. There is an existing 240 outlet with 20 amp breakers and I want to branch off to install another outlet. I realize that I have to install a larger breaker to do this. What size wire must be used to support this installation? The a/c's have a 15 amp draw and are 220v.[?]
Wire size for 40 amp breaker
Collapse
Forum Top GA Ad Widget
Collapse
X
-
The existing wire for a 20 amp breaker should be 12 gauge. You CAN NOT install a larger breaker on 12 gauge wire, this is a dangerous fire hazzard. A 20 amp breaker and 12 gauge wire is the largest wire that can be installed for a residential receptacle other than a dryer or range.
You must run a new circuit from your main panel for the new air conditioner as the present 20 amp breaker will not support both units.Comment
-
each ac unit needs it's own breaker.
But as to your question, 40 amps = # 8 wire.
Did you ever see OHM'S mother in LAW?...... SHOCKING!<i>Did you ever see OHM\'S mother in LAW?</i>...... <font color=\"red\">SHOCKING!</font id=\"red\">Comment