    what wire for what

    ok, 14 gage is for lights, is 12 for the switches?

    Harry R. Plander
  • kactuskid
    Master Journeyman

    • Mar 2004
    • 801

    #2
    They can both be used for wiring circuits, the wire gauge that's used is dependent on the circuit breaker that protects that wire. 14 gauge wire is protected by a 15 amp breaker, and 12 gauge wire is protected by a 20 amp breaker. It's ok to use 12 gauge wire on a 15 amp circuit but I don't advise it, You really want to maintain a consistancy of using the appropriate wire for the proper breaker and not mix the two, if done incorrectly it can lead to a fire hazzard. Here's a link that'll explain a bit more in detail for you.


    If this is a 15 amp breaker then stick with 14 gauge wire. It would also be a good idea if you bought your self a good book to learn about home wiring. The Black and Decker book on home wiring is a good one and will help tremedously in your projects. You can find one at Home Depot or any good book store.

    Comment

    • HayZee518
      Deity

      • Jul 2004
      • 8746

      #3
      I used to wire houses with two gauges of cable 14 and 12. Now a days it doesn't offset the cost very much to use the same cable throughout - so 12 is the norm for everything. Ideally you could use 20 amp breakers on everything but that's up to you, no harm in putting a 12 ga line onto a 15 amp breaker. The cost of a 15 - 20 amp breaker is the same. Just mind you that circuits in a bedroom HAVE to be an "arc-fault" breaker under the new code rules.