  • heating an electrical

    my comment is in the form of a question . when installing heating ducts, can it be placed next to the main circut breaker panal, if so how far or how close should it be,also is there a code that list that in the national electrical code handbook

  • #2
    As long as all of your wires are sheilded, everthing should be fine. A bit more detail on your situation could yeild a different answer though.

    __________________________________________________

    Brandon
    - Have you changed your filter this month? -
    __________________________________________________

    Brandon
    - Have you changed your filter this month? -

    Comment


    • #3
      There are definatly panel clearances that you need to abide by. Think of a box that is 30" across and 36" in front and 66" in height. Nothing else besides the panel is allowed in this space. Here's a link that'll give you the NEC article numbers.