  • sub panel help

    Guys, I am wiring a sub panel in the garage but dont see a ground bus in the panel. I see the neutral bus but and not sure where the bare ground wires should go. I am using #6 wire. Two hot, one white (neutral) and one bare ground. I know where to hook these off of the main panel but not sure where the bare ground goes. I have two breakers in the sub panel. One wired for 110 with a 20 amp breaker and the other wired for 220 on a 30 amp breaker. Where do I attach the bare ground wires if I don't have a ground bus to attach it to.

    I don't think I am supposed to hook the bare ground on the neutral bus, right? Thanks for your help. I will try to get pictures.

  • #2
    very easy - go to a big box store or an electrical supply house and ask for an AUXILLARY ground strip. They sell one that has about 12 openings - cost around three bucks. this installs in any free space inside the panelbox. the bare #6 goes here and all bare earth grounds.

    Comment


    • #3
      Ok, I obviously need to remove the bare ground wire. The subpanel is not hooked to the main yet.

      Am I right, there is not place for bare ground unless I am missing something






      Question is in this lower photo, what are the two blocks with the pinkish looking screws? I am assuming they are to attach the neutral off the main leaving the bar for any additional neutral wires.

      That bar is the one that is for the neutral, correct? I don't see where it is grounded to the panel housing.
      Last edited by delirious; 12-14-2009, 12:45 AM.

      Comment


      • #4
        the two landings to the right part of the panel will accept a bolt in aux ground bar. the neutral strip is not bonded to the panel enclosure in a sub-panel configuration. the red and black large diameter terminates on your main lugs in the sub panel. the pinkish screws may be larger diameter terminations for the bus.

        Comment


        • #5
          It also looks like you have double taps as well, you cannot use the breakers for multiple feeds. Code only permits one wire/breaker.
          like Hayzee says, the ground bar will simply screw onto the inside of the panel at a convenient location.
          Little about a lot and a lot about a little.
          Every day is a learning day.

          Comment


          • #6
            Your picture also shows that you have wired two separate circuits to each breaker. You should only protect one circuit with each breaker. You may need a larger sub-panel with more breakers to properly protect your wiring.

            Comment


            • #7
              Originally posted by Handi-Women LLC View Post
              Your picture also shows that you have wired two separate circuits to each breaker. You should only protect one circuit with each breaker. You may need a larger sub-panel with more breakers to properly protect your wiring.

              Thank you everyone. I will be adding additional breakers today along with the grounding bar. I hope home depot carries them, otherwise I will need to find an electrical supply. I recenlt moved to the area and dont know of one. Much thanks!

              Comment


              • #8
                from what I can see you have five spaces left for GE mini breakers or two full one inch spaces for a GE twin breaker

                Comment


                • #9
                  sniff....sniff...


                  (thanking myself....lol)
                  Little about a lot and a lot about a little.
                  Every day is a learning day.

                  Comment


                  • #10
                    Originally posted by pushkins View Post
                    sniff....sniff...


                    (thanking myself....lol)
                    Got all the material and I think I am good. Again, I appreciate the help.