    Price for 2-2-2-4 Ser Copper

    Happy Holidays to all.

    We have a quick question. We're looking to purchase cable to hookup a sub-panel, but Home Depot, Lowes dont carry that kind of wire,

    Any help awhere in north east New Jersey or on line and the price per foot???

    Thanks in advance
  • HayZee518
    Deity

    • Jul 2004
    • 8746

    #2
    one question: how do you intend to run this wire? through studs or in conduit, underground?
    one company sells 2/4 BX copper at $3.00 a foot.

    Comment

    • JoanK
      New Member

      • Dec 2009
      • 10

      #3
      Originally posted by HayZee518
      one question: how do you intend to run this wire? through studs or in conduit, underground?
      one company sells 2/4 BX copper at $3.00 a foot.
      ...across the ceiling down to the new sub...

      This will be in an attached garage.

      Can you give the name of the company selling the wire????

      JoanK

      Comment

      • HayZee518
        Deity

        • Jul 2004
        • 8746

        #4
        two companies are listed.
        one is: www dot nassaunationalcable dot com
        other is: www dot afcweb dot com

        Comment

        • JoanK
          New Member

          • Dec 2009
          • 10

          #5
          Originally posted by HayZee518
          two companies are listed.
          one is: www dot nassaunationalcable dot com
          other is: www dot afcweb dot com
          Thanks for the info

          JoanK

          Comment

          • Speedy Petey
            Apprentice
            • Nov 2006
            • 214

            #6
            First opff, did you try a real electrical supply house? You will find whatever you need there.

            Second, WHY #2cu ??? This is oversized even for a 100A sub-panel.

            Comment

            • JoanK
              New Member

              • Dec 2009
              • 10

              #7
              Originally posted by Speedy Petey
              First opff, did you try a real electrical supply house? You will find whatever you need there.

              Second, WHY #2cu ??? This is oversized even for a 100A sub-panel.
              The inspector told us that 4-4-4-6 is good for only 80% of 100amps and 2-2-2-4 was recommended.

              Question:

              What size Ser do you recommend????

              Thanks
              JoanK.

              Comment

              • Speedy Petey
                Apprentice
                • Nov 2006
                • 214

                #8
                Originally posted by JoanK
                The inspector told us that 4-4-4-6 is good for only 80% of 100amps and 2-2-2-4 was recommended.
                W...WHAT??

                Wow. It amazes me how clueless some inspectors are, and how they take advantage of unsuspecting folks.

                We would use 2-2-2-4AL SER or 4-4-4-6CU SER. Some inspectors do not allow this and we would use a 90A breaker instead of a 100A. Or just use #1AL or #3CU. Then again, NY follows the NY Resi Code, not the NEC for one and two family dwellings.

                Commercial is completely different.