I have a 220 20 amp circuit feed for a hot water heater. It was old and way over sized for just bathroom sink use.
I just down sized it to a 2.5 gal unit which needs a 110 15amp circuit. When I installed a 110 duplex receptacle, the 220 line was 10 awg w/ 1 white, 1 black and gnd.
I installed the new single slot 110 15 amp Square D breaker where the double slot 20 amp breaker was. I used only one of the two black wires from the old breaker on the new 110 CB.
When I looked at the voltages I am puzzled. I read 100 vac between hot and neutral receptacle slot contacts. I see 19 vac between neutral and gnd and 120 between hot and gnd.
How do I correct this?
BTW: I tried using the other black wire (110 leg?) which was installed on old 220 20 amp CB and got the same reading.
Thanks in advance for your help.
Jay