    Romex in pvc conduit

    I'm wiring a metal frame building. Can romex wire be run inside pvc conduit to protect it from physical damage? If not, please explain.
  • HayZee518
    Deity
    • Jul 2004
    • 8747

    #2
    the code spicifically says that romex or even type UF cable CANNOT be run through any kind of conduit [except for short lengths for mechanical protection] use thhn or thwn stranded conductors.

    Comment

    • StevenW
      New Member
      • Dec 2010
      • 15

      #3
      What would be the reasoning behind this other than it being easier to run individual wires?

      Comment

      • HayZee518
        Deity
        • Jul 2004
        • 8747

        #4
        the reason is heat dissipation. the romex is in a jacketed assembly. it may also fall under "derating" of total amperage of the conductor(s)