I am having problems with the burner not coming on.
The pilot light stays on and is a nice blue color.
I have tested the mv on the line to the thermostat, the mv should be 250 mv when the thermostat is off and 140 mv when it is on. My readings are 223 mv when it is off and 53 mv when it is on.
I have disconnect the thermostat completely and tested and it is 223 mv.
I have taken a paper clip across the connectoin and the burner still does not come on. To me that would tell me the gas valve is bad.
My question is by the manual it should test 250 mv when it is off,
would 223 mv and not the 250 mv make that much of a difference. If that would be the case then my thermocouple is not giving out the right mv and needs to be replaced.