Hi all, hope you had a great Thanksgiving!
Last winter, I noticed that our furnace (2005 Goodman, GMS90904CXA) was triggering the high limit on fairly regular intervals (every 15 minutes or so), in which it would take about 4 minutes to reset. Once the limit is reached, the blower fan continues to run, but no heat is provided since the burner has stopped in order to allow the heat exchanger to cool.
We’ve lived in the house (built in 1989) since Jan 2008, but I never paid much attention to the furnace before last year, so the issue very well could have been occurring the whole time we’ve lived in the house…
So, in order to gear up for this winter, I ended up having an HVAC guy come out a few days ago to perform a tune-up and troubleshoot the high limit issue, in which he concluded the following:
1. Furnace is oversized for the house (90,000 BTUs for a 2,800 sq ft house including basement), and evaporator coil is too narrow for the furnace.
2. Flue/vent currently uses hard 90 deg elbows instead of sweeping 90’s. This could restrict heat from exiting. He recommended that the hard 90s are replaced with sweeping 90’s.
3. Additional return could be installed right outside our furnace room, which could provide additional cooling air to furnace to help prevent heat exchanger from overheating. We currently have six 16” returns through the house.
4. He recommended opening all registers on the main floor. I had nearly half closed in order to force more air into the second level where all of our bedrooms are. After he left, I opened all registers, but still saw high limit being reached.
5. He changed the fan speed from Med to High.
His statements seemed reasonable, but I always like to hear other's thoughts. Do the HVAC tech's recommended corrective actions (sweeping 90’s, additional return, opening all registers) seem like a good next step in eliminating this problem? I hope to avoid sinking money into "potential" solutions that end up not fixing the problem.
One thing I noticed last winter during my own troubleshooting, is that if I pull the air filter 1/3 of the way out, the high limit is typically not triggered. So, lately when we've been heating, I've typically had the filter partially pulled out, which I'm sure is a big no-no. If we pursue adding another return, do you think it will actually allow more air to pass through the filter?
Thanks in advance for any input you can provide!
Last winter, I noticed that our furnace (2005 Goodman, GMS90904CXA) was triggering the high limit on fairly regular intervals (every 15 minutes or so), in which it would take about 4 minutes to reset. Once the limit is reached, the blower fan continues to run, but no heat is provided since the burner has stopped in order to allow the heat exchanger to cool.
We’ve lived in the house (built in 1989) since Jan 2008, but I never paid much attention to the furnace before last year, so the issue very well could have been occurring the whole time we’ve lived in the house…
So, in order to gear up for this winter, I ended up having an HVAC guy come out a few days ago to perform a tune-up and troubleshoot the high limit issue, in which he concluded the following:
1. Furnace is oversized for the house (90,000 BTUs for a 2,800 sq ft house including basement), and evaporator coil is too narrow for the furnace.
2. Flue/vent currently uses hard 90 deg elbows instead of sweeping 90’s. This could restrict heat from exiting. He recommended that the hard 90s are replaced with sweeping 90’s.
3. Additional return could be installed right outside our furnace room, which could provide additional cooling air to furnace to help prevent heat exchanger from overheating. We currently have six 16” returns through the house.
4. He recommended opening all registers on the main floor. I had nearly half closed in order to force more air into the second level where all of our bedrooms are. After he left, I opened all registers, but still saw high limit being reached.
5. He changed the fan speed from Med to High.
His statements seemed reasonable, but I always like to hear other's thoughts. Do the HVAC tech's recommended corrective actions (sweeping 90’s, additional return, opening all registers) seem like a good next step in eliminating this problem? I hope to avoid sinking money into "potential" solutions that end up not fixing the problem.
One thing I noticed last winter during my own troubleshooting, is that if I pull the air filter 1/3 of the way out, the high limit is typically not triggered. So, lately when we've been heating, I've typically had the filter partially pulled out, which I'm sure is a big no-no. If we pursue adding another return, do you think it will actually allow more air to pass through the filter?
Thanks in advance for any input you can provide!