  • Trane XE78 furnace comes on fine then goes out.

    Hello my Trane XE78 comes on fine, heats up and blows warm air. After after some time the fire goes out but the blower keeps on running, and running. I turn off the switch at the thrmostat, wait a few minutes and turn it back on. It comes on and runs fine again.
    Model number is TUD140C960A0

    Found the flame sensor, took it out and cleaned it gently with light sand paper.
    The flame sensor looked fine. Clean when I took it out.
    The furnace is 11 years old.

    Problem persists. After observing the furnace for some time,

    1. Furnace starts up fine.
    2. Runs fine, heating for over a minute.
    3. Reaches some internal temperature, then shuts the flame off, keeping the large forced air blower running circulating heat.
    4. Soon, the internally temperature falls needing more heat. I can see the igniter light up. I see the igniter light three times and go out, but the flames never start. Guess, no gas is released?
    5. During all this time the red light is flashing steadily, about once per second. After the third time the igniter comes on, but fails to light the red light starts flashing twice.


    thanks.

    [V]

  • #2
    Hello mrdb! was the problem in your gas valve?. Just checking since I had the same problem and replaced my own with new valve at approx. $68 bucks. Just wondering.

    Comment


    • #3
      Hello my Trane XE78 comes on fine, heats up and blows warm air. After after some time the fire goes out but the blower keeps on running, and running. I turn off the switch at the thrmostat, wait a minute or so and turn it back on. It comes on and runs fine again for a period of time.
      Model number is TUD060C936A0

      The furnace is 17 years old.

      1. Furnace starts up fine.
      2. Runs fine, heating for about 30 seconds.
      3. Reaches some internal temperature, then shuts the flame off, keeping the large forced air blower blowing cold air.
      4. Soon, the internally temperature falls needing more heat. I can see the igniter light up. I see the igniter light three times and go out, but the flames never start. Guess, no gas is released?

      Any solutions??

      Comment


      • #4
        Originally posted by mrdb View Post
        Hello my Trane XE78 comes on fine, heats up and blows warm air. After after some time the fire goes out but the blower keeps on running, and running. I turn off the switch at the thrmostat, wait a few minutes and turn it back on. It comes on and runs fine again.
        Model number is TUD140C960A0

        Found the flame sensor, took it out and cleaned it gently with light sand paper.
        The flame sensor looked fine. Clean when I took it out.
        The furnace is 11 years old.

        Problem persists. After observing the furnace for some time,

        1. Furnace starts up fine.
        2. Runs fine, heating for over a minute.
        3. Reaches some internal temperature, then shuts the flame off, keeping the large forced air blower running circulating heat.
        4. Soon, the internally temperature falls needing more heat. I can see the igniter light up. I see the igniter light three times and go out, but the flames never start. Guess, no gas is released?
        5. During all this time the red light is flashing steadily, about once per second. After the third time the igniter comes on, but fails to light the red light starts flashing twice.


        thanks.

        [V]
        I don't have a book to check you red lite code. When the glow
        bar get hot you should get about 6 to 8 sec. of gas valve opening. You would have to test to see if you are getting the 24 volt power at that time.
        If you have gas coming to the valve and you get power and no gas to burners then it in the gas valve. If you do not get any power to the gas valve
        it would be a problem in the board. paul