I have a gas fireplace which utilizes a milli volt control system.
The main burner will not light- no problems with the pilot light.
I have checked the millivolt readings on the thermopile with the following results:
Gas valve ON, Pilot light ON, Wall switch OFF thermopile = 650mv
Gas valve ON, Pilot light ON, Wall switch ON thermopile = 3mv
All wiring connections check good, Wiring and switch resistance good.
Switch connections jumpered at gas valve- no main burner light up
With gas valve On, Pilot light On, and wall switch On reading at gas valve accross thermopile connections is supposed to be 100mv min.
It is obvious that with a reading of 3mv the valve will not open.
Is it possible to have a bad thermopile that reads normal ( 650mv ) with no load and then have it drop to 3mv when heat is called for, or is it likely that there is a fault within the gas valve which is drawing down the voltage to the point that it will not open the valve.
Thanks
The main burner will not light- no problems with the pilot light.
I have checked the millivolt readings on the thermopile with the following results:
Gas valve ON, Pilot light ON, Wall switch OFF thermopile = 650mv
Gas valve ON, Pilot light ON, Wall switch ON thermopile = 3mv
All wiring connections check good, Wiring and switch resistance good.
Switch connections jumpered at gas valve- no main burner light up
With gas valve On, Pilot light On, and wall switch On reading at gas valve accross thermopile connections is supposed to be 100mv min.
It is obvious that with a reading of 3mv the valve will not open.
Is it possible to have a bad thermopile that reads normal ( 650mv ) with no load and then have it drop to 3mv when heat is called for, or is it likely that there is a fault within the gas valve which is drawing down the voltage to the point that it will not open the valve.
Thanks