20 yr old Amana would not run this morning about 6 am. Began t/s by simply turning fan to "on " position. Would not run fan. Went to air handler in attic. Checked volts to blower motor leads. Each of two leads read 120 vac to ground, BUT read ZERO volts to each other, so apparently they both had the same 120 volt phase on them.
After fooling around with motor leads about 9 am the system suddenly came alive and began working with 240 vac across the motor leads. Who knows for sure, but I do not think there were any loose connections that we "fixed" by fooling with them. I am not a REAL HP tech, but I suspect that a component in the compressor unit outside was temporarily "frozen", stuck, or something and was preventing the air handler from operating.
I suspect this will happen again, and am looking for advice on how to find the problem.
Thanks for any assistance.
After fooling around with motor leads about 9 am the system suddenly came alive and began working with 240 vac across the motor leads. Who knows for sure, but I do not think there were any loose connections that we "fixed" by fooling with them. I am not a REAL HP tech, but I suspect that a component in the compressor unit outside was temporarily "frozen", stuck, or something and was preventing the air handler from operating.
I suspect this will happen again, and am looking for advice on how to find the problem.
Thanks for any assistance.