Hello folks!  Yesterday after coming home from work I noticed the house was a bit chilly.  Noticed air was being blown but it was only cold air.
 
The following is what I know and what I have looked at.
 
1) Heat is commanded vent motor fires up. After about 6 seconds vent motor shuts off and main fan blower kicks on. No flame, no ignition...
 
2) Error LED flashes 6 times. Supposed to mean 115VAC reveresed polarity or bad ground.
 
3) I checked all powerI have 120VAC.. getting to the circuit board. I have 120VAC on Primary of transformer and 27VAC on secondary being fed to CB.
 
4) I have no voltage ever getting sent to Gas valve or ignitor. Have clean filter shorted out safety switched one at a time same results.
 
This one is bugging me I am not sure what the cause would be... I am thinking it may be the Circuit board but I don't know. About ready to give in and call HVAC tech but any other advice would be welcome.
 
Regards,
Tom Spokane, WA
					The following is what I know and what I have looked at.
1) Heat is commanded vent motor fires up. After about 6 seconds vent motor shuts off and main fan blower kicks on. No flame, no ignition...
2) Error LED flashes 6 times. Supposed to mean 115VAC reveresed polarity or bad ground.
3) I checked all powerI have 120VAC.. getting to the circuit board. I have 120VAC on Primary of transformer and 27VAC on secondary being fed to CB.
4) I have no voltage ever getting sent to Gas valve or ignitor. Have clean filter shorted out safety switched one at a time same results.
This one is bugging me I am not sure what the cause would be... I am thinking it may be the Circuit board but I don't know. About ready to give in and call HVAC tech but any other advice would be welcome.
Regards,
Tom Spokane, WA