I have an Amana DMS81405DHA Heater/AC split unit that has the following circuit board: White-Rodgers 4586-b - The secondary fan (the little fan above the burners that continues to blow after heat shuts off so remaining heat dissipates) will not shut off and the DS1 light is lite up on the board. I have check thermostats and wiring down to the board. Any ideas what it could be and how to fix it?
Announcement
Collapse
No announcement yet.
HELP - Small Upper Blower wont shut off
Collapse
Forum Top GA Ad Widget
Collapse
X
-
Originally posted by drmustang68 View PostI have an Amana DMS81405DHA Heater/AC split unit that has the following circuit board: White-Rodgers 4586-b - The secondary fan (the little fan above the burners that continues to blow after heat shuts off so remaining heat dissipates) will not shut off and the DS1 light is lite up on the board. I have check thermostats and wiring down to the board. Any ideas what it could be and how to fix it?
relay on your board has the points stuck together. Is so you will have to replace the board. later paul
-
Originally posted by drmustang68 View PostThank you very much for your response.
How can I identify the post purge relay on the board?
Jay
and it is not a replaceable part so you would have to replace the board itself.
later paul
Comment
-
BTW: I was just continuing my diagnostics and found that the heat would not come on and when heat was ordered, the board DSL blink code said the pressure switch was stuck closed - Even though the switch seems functional (I can hear it opening and closing freely) - I bypassed the switch, the heat came on as it should, but the Draft Inducer motor is still continuously running so I think you are correct about the post purge relay being bad on the board. Thoughts?
Comment
-
Originally posted by drmustang68 View PostBTW: I was just continuing my diagnostics and found that the heat would not come on and when heat was ordered, the board DSL blink code said the pressure switch was stuck closed - Even though the switch seems functional (I can hear it opening and closing freely) - I bypassed the switch, the heat came on as it should, but the Draft Inducer motor is still continuously running so I think you are correct about the post purge relay being bad on the board. Thoughts?