I've got a carrier heat pump unit that's about 5 years old. I've self-maintained this unit since it went out of warranty, but this problem has me baffled.
Basically about 2 weeks ago there was a series of storms and as usual we had a lot of intermittent power problems. At one point , someone heard what could be described as a clacking noise inside the air handler and the unit then went dead.
I proceeded to debug and found that the transformer was not registering any low side voltage, but 220 was at the high side. It was strange, because this unit has a 5 amp fuse on the fan control board which appears to be right in line after the transformer (just before the fan relay). This fuse was not and still isn't blown.
So, I ordered two generic type transformers (matching specs) off Ebay. I hooked one up and popped back in the inside disconnect. Immediately I heard a pop and the inline 2 AMP fuse that came with the new transformer had blown Still the 5 amp fuse on the control board in intact. The new transfomer also now appears to be fried as I don't get any low side voltage.
I've since checked and rechecked every wire and connection I could all the way out to the outside unit and even inside to see if I could find any chafing. I'm not sure , but I also checked resistance across the contactor with my meter set at 20 ohms. It did register some resistance. I have had problems with the contactor mechanically in the past and have cleaned/filed the contacts on it. The unit outside turns on if I manually push the contactor in and I believe the compressor and fan run.
What else could be wrong here? Is it possible that the 2 amp fuse is not big enough for this unit? Also, I don't know what the point of the protection fuse is when the transformer blows anyway? I have one more new transformer I ordered as I figured I might need it. Please give me some ideas so I don't have to blow it too. Really can't afford an AC tech right now Thanks much!
Basically about 2 weeks ago there was a series of storms and as usual we had a lot of intermittent power problems. At one point , someone heard what could be described as a clacking noise inside the air handler and the unit then went dead.
I proceeded to debug and found that the transformer was not registering any low side voltage, but 220 was at the high side. It was strange, because this unit has a 5 amp fuse on the fan control board which appears to be right in line after the transformer (just before the fan relay). This fuse was not and still isn't blown.
So, I ordered two generic type transformers (matching specs) off Ebay. I hooked one up and popped back in the inside disconnect. Immediately I heard a pop and the inline 2 AMP fuse that came with the new transformer had blown Still the 5 amp fuse on the control board in intact. The new transfomer also now appears to be fried as I don't get any low side voltage.
I've since checked and rechecked every wire and connection I could all the way out to the outside unit and even inside to see if I could find any chafing. I'm not sure , but I also checked resistance across the contactor with my meter set at 20 ohms. It did register some resistance. I have had problems with the contactor mechanically in the past and have cleaned/filed the contacts on it. The unit outside turns on if I manually push the contactor in and I believe the compressor and fan run.
What else could be wrong here? Is it possible that the 2 amp fuse is not big enough for this unit? Also, I don't know what the point of the protection fuse is when the transformer blows anyway? I have one more new transformer I ordered as I figured I might need it. Please give me some ideas so I don't have to blow it too. Really can't afford an AC tech right now Thanks much!