    I have a one ton mini split ductless heat pump (Heat Controller Inc. MSH-012B). Recently, I started getting a main breaker trip (110v, 15A) after a few minutes of system operation.

    It appears that the outdoor unit fan motor is running slow (330 rpm versus 800 rpm spec) and I have a fault code of a slow ( one flash every 3 seconds) flashing green light (LED91) on the evaporator's temperature control circuit board (PWB ASSY:6871AQ1050) . Perhaps without proper heat removal the compressor eventually exceeds the 15A breaker (normal current draw is 11A) and the unit shuts down to protect itself (thankfully).

    I can't find the fault code list for this unit ( 8 years old) so I'm not sure if it is the motor or something with the control circuit. I checked the voltage to the motor and it reads 120v which should be fine.

    I pulled the motor and it turns free, not signs of damage. I wire brushed the mounting surfaces just in case there was grounding issue but after reinstalling the motor the same problem persists.

    To make matters a little more challenging, the one on-line source that I could find for a replacement motor indicates that it is not in stock. The motor is a LG 4681AR1392J.

    Can anyone tell me what the slow flashing error code for this machine is telling me?

    If it is the motor, does anyone know of a suitable replacement?

    Thanks in advance for any advice!

    Larry
    Last edited by Premium2000; 07-18-2010, 03:03 PM. Reason: Added more information

  • #2
    Originally posted by Premium2000 View Post
    I have a one ton mini split ductless heat pump (Heat Controller Inc. MSH-012B). Recently, I started getting a main breaker trip (110v, 15A) after a few minutes of system operation.

    It appears that the outdoor unit fan motor is running slow (330 rpm versus 800 rpm spec) and I have a fault code of a slow ( one flash every 3 seconds) flashing green light (LED91) on the evaporator's temperature control circuit board (PWB ASSY:6871AQ1050) . Perhaps without proper heat removal the compressor eventually exceeds the 15A breaker (normal current draw is 11A) and the unit shuts down to protect itself (thankfully).

    I can't find the fault code list for this unit ( 8 years old) so I'm not sure if it is the motor or something with the control circuit. I checked the voltage to the motor and it reads 120v which should be fine.

    I pulled the motor and it turns free, not signs of damage. I wire brushed the mounting surfaces just in case there was grounding issue but after reinstalling the motor the same problem persists.

    To make matters a little more challenging, the one on-line source that I could find for a replacement motor indicates that it is not in stock. The motor is a LG 4681AR1392J.

    Can anyone tell me what the slow flashing error code for this machine is telling me?

    If it is the motor, does anyone know of a suitable replacement?

    Thanks in advance for any advice!

    Larry
    Does that motor have its own start capacitor? If its a bad capacitor the motor will run slow like that. You might have to check with a dealer for a motor replacement. Later Paul

    Comment


    • #3
      Thanks Paul.

      The unit does use a dual run capacitor rated at 6/45uF @ 370/400VAC.

      While it does not show signs of damage, it seems like the mostly likely source of the problem.

      I can't seem to find an exact replacement. There are dual run capacitors rated at 5/45, 7/45 and 7.5/45 (370V or 440V). Can I use one of these? If so, which rating would be the best suited?

      Thanks,

      Larry

      Comment


      • #4
        Originally posted by Premium2000 View Post
        Thanks Paul.

        The unit does use a dual run capacitor rated at 6/45uF @ 370/400VAC.

        While it does not show signs of damage, it seems like the mostly likely source of the problem.

        I can't seem to find an exact replacement. There are dual run capacitors rated at 5/45, 7/45 and 7.5/45 (370V or 440V). Can I use one of these? If so, which rating would be the best suited?

        Thanks,

        Larry
        I don't know about using a different capacitor, i always order
        up the right one if i don't already have it it my service truck. Later Paul

        Comment


        • #5
          Thanks,

          I think I found a supplier with a direct replacement. Hopefully, that will solve the problem.