    recessed lights inside duct??

    I am in the process of putting a bathroom in my basement and have had to drywall around ducts. A friend told me that it would be OK to install a recessed light right inside the heating/cooling duct as it passes right over the top of my lav/mirror. Can someone tell me if this is acceptable/advisable?
  • JakeOfAllTrades
    Handyman
    • Jul 2005
    • 36

    #2
    I'm no electrician, but I would not put a light (or any other electric device, for that matter) inside the ductwork.



    -----------------------------------------------------------------------------------------------------------------------------------------------
    <center></center>

    Comment

    • LazyPup
      Deity

      • Apr 2004
      • 2316

      #3
      it not only is not advisable, it is code prohibited.

      Comment

      • HayZee518
        Deity

        • Jul 2004
        • 8746

        #4
        No way! Putting a light fixture into a duct is like putting non plenum cable inside a duct. Against fire code regulations and the NEC.

        Comment

        • lonestarheir
          Handyman
          • Jul 2005
          • 137

          #5
          Whoever told you that should be hung by there toes!!!! Not only should you not do it for the reasons listed above, but just think about how much heat a can light puts off, now put that in an area where the temps are about 20 degrees lower than the room temp. What happens when you apply cold air to a hot surface.....bingo, condensation. do you really want a light that is pouring water out of it while you are standing in the shower???

          Have you changed your filter this month?
          __________________________________________________

          Brandon
          - Have you changed your filter this month? -