Baseboard heater installation

Collapse

Forum Top GA Ad Widget

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • rajrac
    New Member
    • Apr 2006
    • 3

    #1

    Baseboard heater installation

    I'm very new at this and like to know if I can install a baseboard on the inside wall instead of outside wall. i can access my inside wall from the other side. The heater is 1000watts 240v and using 12/2 wire.
  • HayZee518
    Deity
    • Jul 2004
    • 8747

    #2
    1000 watts divided by 240 gives you 4.167 amps. you'd be safe to use 14/2 on a 15 amp breaker. If your upper and lower walls align with each other, maybe you can snake a wire in between the walls.

    Comment

    • Hube
      Journeyman
      • Nov 2003
      • 453

      #3
      Rajrac;your question was..." can i install on inside wall...' and the answer is YES, no problem.
      And use the 12/2 wire and you will be better off.

      Comment

      • rajrac
        New Member
        • Apr 2006
        • 3

        #4
        baseboard heater

        Thank You guys for a quick reply. i will try it on the weekend.

        Comment