    If you have a lamp rated 60 watts that normally operates on 240 volts, what would be the current draw if it operates on 120 volts?

  • #2
    Whatever math I did was wrong.

    This is the best I could come up with.
    I'll stick to doing things how I know.
    Last edited by Speedy Petey; 03-26-2008, 06:11 AM.

    Comment


    • #3
      Unless I am doing something wrong, I get .5A

      Comment


      • #4
        The POWER represented by P never changes. P=EI - The E or voltage is a variable and I the current is variable.
        60 divided by 240 equals a quarter amp. 60 divided by 120 equals a half amp. Because you are operating the 240 bulb at half its rated voltage the amperage is double its normal operating amperage. Therefore the bulb operates at a half amp.

        Comment


        • #5
          SO then why did you ask?
          Was this some sort of test?

          I always knew a lamp worked at half wattage at half voltage, so I did the math to see if I my thinking was correct and came up different. I was wrong because I did the wrong math. I thought into it too much.
          I should have stuck to my instinct.

          Comment


          • #6
            Just to make sure I have this straight, the 60 watt lamp at 240 volts glows at 60 watts (naturally), so at 120 volts it would glow at only 15 watts a 1/4 of it's rated output with 1/2 of the power supply ?
            Little about a lot and a lot about a little.
            Every day is a learning day.

            Comment


            • #7
              No, no test. Just a problem for discussion. All the incandescent nightlights I have in my house are 240 volt 6S6 bulbs. I put these in - in the year 2000 and they are still working. The 6S6 bulb has a base like the old Xmas tree bulbs. The 60 watt bulb operating at 240 volts draws a quarter amp. If you operate it at 120 volts the wattage reduces by one-half. The current is the same a quarter amp. 60 divided by 240 = .25. 30 divided by 120 = .25.

              Comment


              • #8
                No Push.

                60w@ 240v = 30w@120v

                I over though it and confused myself over something extremely simple.

                Comment


                • #9
                  Alot of people do that. They don't think "out of the box" Don't you find many people complicating something simple? Engineers are good for that. Take a simple switch and add a bunch of relays - Boom! complicated circuits.

                  Comment


                  • #10
                    Thanks speedy....Now I'm unconfused.
                    Little about a lot and a lot about a little.
                    Every day is a learning day.

                    Comment


                    • #11
                      Nuther question........
                      Say you have a common residential dryer operating at 150 feet from the panelbox. Assuming the dryer is a 2.7Kw. What is the size of the feeder (voltage drop no more than 3% per hundred feet)

                      Comment


                      • #12
                        #10cu @ 150 feet @ 240v @ 11.25 amps = 1.74375% voltage drop

                        Even with an imbalance from the 120v items it is well below 3%

                        Comment


                        • #13
                          1 conductor(s) per phase utilizing a 12 AWG Copper conductor will limit the voltage drop to 2.43% or less when supplying 11.2 amps for 150 feet on a 240 volt system.

                          For Engineering Information:

                          * 20 Amps Rated ampacity of selected conductor
                          * 1.9029 Ohms Resistance (Ohms per 1000 feet)
                          * 0.054 Ohms Reactance (Ohms per 1000 feet)
                          * 7.2 volts maximum allowable voltage drop at 3%
                          * 5.83 Actual voltage drop loss at 2.43% for the circuit
                          * 0.9 Power Factor

                          Comment


                          • #14
                            It's an electric clothes dryer. I'd still use #10.

                            Comment


                            • #15
                              For a regular circuit of: #12 @ 150' @ 240v with 11.25 amps I get 6.6825 volt drop equaling 2.784375%