Announcement

Collapse
No announcement yet.

Panel torque

Collapse

Forum Top GA Ad Widget

Collapse
X
 
  • Filter
  • Time
  • Show
Clear All
new posts

  • Panel torque

    Hello, I am looking for the torque requirements for the pannel box . do you know them or know someone who does? I also need the tourqe requriments for 3 ott wire. Thank you

  • #2
    Wire does not have a torque spec, terminations do.

    They will be on the panel label or the termination itself.

    Comment


    • #3
      15 in-lb for terminals

      Comment


      • #4
        Originally posted by HayZee518 View Post
        15 in-lb for terminals
        I am not sure this is the correct torque for a 200A breaker.

        Comment


        • #5
          Originally posted by Speedy Petey View Post
          Wire does not have a torque spec, terminations do.

          They will be on the panel label or the termination itself.
          so it will be on the breaker?

          Comment


          • #6
            so the toruque requriment will be on the breaker itself ?

            Comment


            • #7
              doesnt it depend on what quage of wire you have for the torque/

              Comment


              • #8
                I looked on the panel sticker of a 200 amp panel - 15 lbs-in for the breaker.

                Comment


                • #9
                  Hmmm, doesn't sound right to me. I'll look myself.

                  Comment


                  • #10
                    Branch circuit breakers, depending on brand, size and wire capacity: 15-30 in/lb

                    The one 200A main breaker I grabbed was 180in/lb for #2-300mcm.

                    Comment


                    • #11
                      Milbank site www dot milbankmfg dot com - 350 Kcmil through #6 - 250 lb-in Line - Neutral

                      Comment

                      Working...