    Panel torque

    Hello, I am looking for the torque requirements for the pannel box . do you know them or know someone who does? I also need the tourqe requriments for 3 ott wire. Thank you
  • Speedy Petey
    Apprentice
    • Nov 2006
    • 214

    #2
    Wire does not have a torque spec, terminations do.

    They will be on the panel label or the termination itself.

    Comment

    • HayZee518
      Deity
      • Jul 2004
      • 8747

      #3
      15 in-lb for terminals

      Comment

      • Speedy Petey
        Apprentice
        • Nov 2006
        • 214

        #4
        Originally posted by HayZee518
        15 in-lb for terminals
        I am not sure this is the correct torque for a 200A breaker.

        Comment

        • Kimberley Johnson
          New Member
          • Oct 2008
          • 6

          #5
          Originally posted by Speedy Petey
          Wire does not have a torque spec, terminations do.

          They will be on the panel label or the termination itself.
          so it will be on the breaker?

          Comment

          • Kimberley Johnson
            New Member
            • Oct 2008
            • 6

            #6
            so the toruque requriment will be on the breaker itself ?

            Comment

            • Kimberley Johnson
              New Member
              • Oct 2008
              • 6

              #7
              doesnt it depend on what quage of wire you have for the torque/

              Comment

              • HayZee518
                Deity
                • Jul 2004
                • 8747

                #8
                I looked on the panel sticker of a 200 amp panel - 15 lbs-in for the breaker.

                Comment

                • Speedy Petey
                  Apprentice
                  • Nov 2006
                  • 214

                  #9
                  Hmmm, doesn't sound right to me. I'll look myself.

                  Comment

                  • Speedy Petey
                    Apprentice
                    • Nov 2006
                    • 214

                    #10
                    Branch circuit breakers, depending on brand, size and wire capacity: 15-30 in/lb

                    The one 200A main breaker I grabbed was 180in/lb for #2-300mcm.

                    Comment

                    • HayZee518
                      Deity
                      • Jul 2004
                      • 8747

                      #11
                      Milbank site www dot milbankmfg dot com - 350 Kcmil through #6 - 250 lb-in Line - Neutral