    Elmwood sensor....

    Working on an old, CleanBurn waste oil furnace. I found this sensor does not have continuity, so I suspect it is no good. But how do I tell? I don't know if it's normally open or normally closed....the info on it is:
    Elmwood 3004-5-8 L220 81/47
    I did look up Elmwood anything and did not find what I need. Does the L220 mean that's it's heat limit? What might the 81/47 mean?
  • SeattlePioneer
    New Member

    • Feb 2009
    • 15

    #2
    Yes, it a limit switch that should open and shut off the burners at 220F.

    Comment

    • mrcaptainbob
      King

      • Jan 2004
      • 1746

      #3
      Limit sensor....

      Thanks, Seattle Pioneer. That confirms my suspicion. But that leaves me with another question. How can I tell if it's normally open or normally closed? Also, are sensors like this used to control on/off situations? That is, to keep the item it's protecting from going past the temperature cutoff? In other words....how many cycles is a typical sensor good for?

      Comment

      • SeattlePioneer
        New Member

        • Feb 2009
        • 15

        #4
        Limit switches are normally closed and open upon reaching the rated temperature. Some may be manual reset that remain closed until a button is pushed, otherwise they reset when the temperature declines twenty degrees or so below the rated maximum. They will typically cycle on and off as rated indefinitely.

        Comment

        • mrcaptainbob
          King

          • Jan 2004
          • 1746

          #5
          Sensor....

          As I suspected, SeatllePioneer. Thanks for the confirmation.