I just purchased a 10" diameter Tjernlund duct fan that I want to install at the end of a teed off main blower duct work. It is a 110 volt fan. I have already run a 12-2 line from where the fan will be mounted all the way back to my Payne 4 ton air handler. I thought this would be the way to go so that the booster fan would be controlled only when the main air handler fan would cycle on and off. When I started to look at how the main blower fan was wired I then realized that the motor is a 230 volt unit. I now need to know if there is a way to find a 120 volt connection that is activated when the fan comes on. What I have found is that the black wire from the main blower motor goes to a relay mounted onto a PC board. I believe this is the high speed connection.The other yellow wire goes to a transformer which I believe is the common leg. There are two other wires. red and blue, that are capped off. I believe these two capped off wires are the low and medium speed connections of the 3 speed motor. So is there a way to hook up this booster fan to the main motor?
Announcement
Collapse
No announcement yet.
Adding Duct Fan
Collapse
Forum Top GA Ad Widget
Collapse
X
-
Originally posted by HayZee518 View Postthen there should be no problem. just parallel the new wiring with the existing blower motor. when it kicks in the aux will also start. the relay should handle the slight increase in amperage.
Comment
-
ok, I didn't read your complete posting. Yeah, slight problem.
you'll need a 240 volt to 120 volt step down transformer. Now to figure out the size of the xfmr.
How many watts or amps does the fan draw? Once I have this info I can figure out the size [in Kva] for the transformer.
Comment
-
Originally posted by HayZee518 View Postok, I didn't read your complete posting. Yeah, slight problem.
you'll need a 240 volt to 120 volt step down transformer. Now to figure out the size of the xfmr.
How many watts or amps does the fan draw? Once I have this info I can figure out the size [in Kva] for the transformer.
Thanks
Comment
-
go to an electrical supply house [not a big box store] and ask for a dry type distribution transformer 50 va, 240 volt to 120 volt. the primary is annotated as H1 - H2, the secondary is X1 - X2. Your 240 volt will go in on H1-H2, your load will come off on X1-X2.
Comment
-
Originally posted by HayZee518 View Postgo to an electrical supply house [not a big box store] and ask for a dry type distribution transformer 50 va, 240 volt to 120 volt. the primary is annotated as H1 - H2, the secondary is X1 - X2. Your 240 volt will go in on H1-H2, your load will come off on X1-X2.
Comment
-
the other alternative would be to run an additional 120 volt line to your furnace to a relay, rated at 240 volts on the coil and use the common to normally open contact to switch the 120 volt hot to the motor. I priced a few transformers and they are out of this world! the relay coil would be in parallel with the blower motor to close when [IT] turned on. the relay's common to normally open contacts would close feeding 120 volts to the aux blower.
Comment
-
Originally posted by HayZee518 View Postthe other alternative would be to run an additional 120 volt line to your furnace to a relay, rated at 240 volts on the coil and use the common to normally open contact to switch the 120 volt hot to the motor. I priced a few transformers and they are out of this world! the relay coil would be in parallel with the blower motor to close when [IT] turned on. the relay's common to normally open contacts would close feeding 120 volts to the aux blower.
Thanks
Comment
-
Originally posted by HayZee518 View Posthere you'll find a drawing for the relay. its cheaper than a transformer and does essentially the same thing BUT with the addition of another 120 volt circuit.[ATTACH=CONFIG]2628[/ATTACH]
Thanks
Comment
-