I just purchased a 10" diameter Tjernlund duct fan that I want to install at the end of a teed off main blower duct work. It is a 110 volt fan. I have already run a 12-2 line from where the fan will be mounted all the way back to my Payne 4 ton air handler. I thought this would be the way to go so that the booster fan would be controlled only when the main air handler fan would cycle on and off. When I started to look at how the main blower fan was wired I then realized that the motor is a 230 volt unit. I now need to know if there is a way to find a 120 volt connection that is activated when the fan comes on. What I have found is that the black wire from the main blower motor goes to a relay mounted onto a PC board. I believe this is the high speed connection.The other yellow wire goes to a transformer which I believe is the common leg. There are two other wires. red and blue, that are capped off. I believe these two capped off wires are the low and medium speed connections of the 3 speed motor. So is there a way to hook up this booster fan to the main motor?
Adding Duct Fan
Collapse
Forum Top GA Ad Widget
Collapse
X
-
If I do this would I be supplying 230 volts to the aux motor which is only rated for 120 volts?Comment
-
ok, I didn't read your complete posting. Yeah, slight problem.
you'll need a 240 volt to 120 volt step down transformer. Now to figure out the size of the xfmr.
How many watts or amps does the fan draw? Once I have this info I can figure out the size [in Kva] for the transformer.Comment
-
The fan motor is 1.8 amps or about 220 watts.ok, I didn't read your complete posting. Yeah, slight problem.
you'll need a 240 volt to 120 volt step down transformer. Now to figure out the size of the xfmr.
How many watts or amps does the fan draw? Once I have this info I can figure out the size [in Kva] for the transformer.
ThanksComment
-
go to an electrical supply house [not a big box store] and ask for a dry type distribution transformer 50 va, 240 volt to 120 volt. the primary is annotated as H1 - H2, the secondary is X1 - X2. Your 240 volt will go in on H1-H2, your load will come off on X1-X2.Comment
-
Thanks again for all your help. To keep the transformer out of the air handler, when it finally goes and needs to be replaced, I was thinking of mounting the transformer into a utility box away from the air handler and just then run the 240 volt wires from the handler into the utility box which I would also add two ventilation round openings for air flow around the transformer. I don't want an AC installer to start telling me more money for the install because he would have to remount the transformer into the new air handler.Comment
-
the other alternative would be to run an additional 120 volt line to your furnace to a relay, rated at 240 volts on the coil and use the common to normally open contact to switch the 120 volt hot to the motor. I priced a few transformers and they are out of this world! the relay coil would be in parallel with the blower motor to close when [IT] turned on. the relay's common to normally open contacts would close feeding 120 volts to the aux blower.Comment
-
I did find one on ebay as new for $34.00 with free shipping that I just purchased.the other alternative would be to run an additional 120 volt line to your furnace to a relay, rated at 240 volts on the coil and use the common to normally open contact to switch the 120 volt hot to the motor. I priced a few transformers and they are out of this world! the relay coil would be in parallel with the blower motor to close when [IT] turned on. the relay's common to normally open contacts would close feeding 120 volts to the aux blower.
ThanksComment
-
Let me try that out. If my relay has different tabs than what you displayed I will get back to you.
ThanksComment
-