    small home boiler

    On a small residential boiler is a low water cut system required?

    Tom
  • HayZee518
    Deity
    • Jul 2004
    • 8747

    #2
    I don't know if it's required but I wouldn't run it without one!

    Comment

    • akaothermick
      Absolutely incompetent
      • Jan 2014
      • 141

      #3
      The boiler code requires a low water cutoff, without it you could do serious damage to a boiler, and risk an explosion if any other safety relief system did not function to its required capacity.
      Last edited by akaothermick; 10-22-2015, 09:06 PM.

      Comment

      • hawkins111
        Master Journeyman
        • Mar 2010
        • 752

        #4
        The reason I ask is that here in Alaska I have never seen a LWCO on a home boiler. Most of the install packages state "Optional". I did see one installed the other day, but the wiring was not connected. This whole installation was a mess anyway and needs so much work to make it right, even though it is only 6 months old. I did see some of the code for NH and VT that do require LWCO for any hot water boiler. My boiler mentor is off hunting so I can't get his point. Thanks, Tom

        Comment

        • akaothermick
          Absolutely incompetent
          • Jan 2014
          • 141

          #5
          Local codes take precedence and generally follow industry, and national standards, but not always the case, a low water cutoff will allow a boiler to survive a draining incident.