I have a noisy louvered register in my great room that is attached to a large supply duct. The duct is short and close to the furnace and the air handler. The register which is vertically mounted at about 10'-0" A.F.F. sort of rattles and buzzes when the air handler is going. Any recommendations to reduce the noise?
Announcement
Collapse
No announcement yet.
Noisy Supply Register
Collapse
Forum Top GA Ad Widget
Collapse
X
-
Air, like all fluids will take the path of least resistance. This register is close to the airhandler and offers the first point of discharge, therefore the least resistance. The noise is then being caused by an excessive velocity of air discharging from this register.
There should be a balancing damper on the duct from the main trunk to the register. Closing that damper slightly will throttle the air flow to permit a balanced pressure between the register and the main trunk downstream from that point. If you have no balancing damper you can close the register down a bit to reduce the airflow, but that may result in a higher velocity of discharge which would cause a vibration and whistling effect.
-
This is a common follow up on new installations so you should have no problem getting it corrected by your installer.
If there is not a throttling damper on that run, it is a very simple operation to install one. I am attaching an illustration of the damper and method of installing it.