I had a post about this boiler before, well i put everything on except the one release valve and turned the boiler on. Well the temp went up, high and fast. actually its still going up after i turned the boiler off as i type this. The problem im having is that the pressure needle never moved but the temp was over 120 degrees. Is this normal?
Boiler problem
Collapse
Forum Top GA Ad Widget
Collapse
X
-
Well sometimes the pressure gage sticks, let it go on up to 180 and see what it does. If your expansion tank is a good size one, then the pressure would not go up much at all going from 70 to 120. Under a normal start when boiler is cold it would have from 10 to 14 lbs. Depending on how many gal. of waterI had a post about this boiler before, well i put everything on except the one release valve and turned the boiler on. Well the temp went up, high and fast. actually its still going up after i turned the boiler off as i type this. The problem im having is that the pressure needle never moved but the temp was over 120 degrees. Is this normal?
in your system and how large your expansion is it will go up in pressure as it heats and the water expands. It could go to 16 to 25 lbs. Paul -
In my last post i told you what the pressure should be, so if your pressure is right, then turn it on and let it come up to 180 degrees and see what you pressure is at that point. PaulComment