Originally posted by bml999
View Post
you don't have a flame censer, so not sure what you have. You also could have a week magnet in your gas valve. When you lite the pilot let it burn a few min. then blow it out and see how long it takes for the gas valve to click out. It should take a min. If it clicks out real fast then your ether have a week magnet, dirty pilot. bad thermocouple. or not in place..
When you fire the furnace, watch the burners and when the blower comes,
see if the burner flame is distorted or floats down around the burners.
If it does, call a tech right away, because this can mean you have a plugged
heat exchanger or it is cracked. If you have a thermocouple then you can
buy a pilot re-lite control. I know Honeywell makes them. Later Paul

Leave a comment: