My 422 is 12 yrs old, in 900SF garage office space with 275 external tank. Had the blower motor replaced 7 yrs ago and no other service than that.
It started shutting down last year, then this year every week or so it was shutting down so decided to have it rebuilt by Perfect Plumbing Lyman Me for $500 (kit was $300 so I felt the $200 investment wsa justified to be done by a pro who knows these units) I watched the entire process - new burner pot, ring all gaskets, cleaned and vacced the heat exchanger - lots of soot came out. Also replaced the oring on the damper assy as it was cracked, and filed down the tabs on the damper to prevent sticking. Also cleaned the small sump etc..
They checked the air flow with a manometer was low so they removed the restrictor donut and readings were acceptable (I think just under 2 on low and under 4 on high) It wasnt buring a nice blue flame so they came back again and checked the air and said this was the best they could do.. It would burn 90% blue 10% yellow on low, 75/25 blue/yellow on Med and 60/40 yellow/blue on high still not great..Also fume plumes from exhaust on shutdown.
Anyway three weeks after rebuild shut off again, restarted and it functioned until last week, -10 Mon AM, it was off again, so I tried to start and click-click - from reading here I decucted no fuel, so replaced the tank filter outside - it had 1/4" frozen gunk in base. While filter was off drained some kero - it was clear/red no water so installed the filter and bled the air out.
Now to the 422 click click a few times and alls good and running again, low, med and high, but flames still arent good. So on low I take off inlet air and play restrictor with my hand, and by reducing air its 95% blue on low! Great, so I put donut back in now 95% blue on low, with tinges of yellow at 10 and 2 oclock via the sight glass. On Med its 75% blue with yellow tips - still acceptable, on high mostly yellow with blue at the base. The damper is functioning properly as I can hear it click in/out as it cycles from high to lower.
Then on shutdown once the blower stops the exhaust fumes raw kerosene for 4-5 minutes.. not good as this is carboning up the HX I think..and also this points to solenoid pump not shutting down cutting off fuel I think maybe its dirty/got junk in it...
So today I removed solenoid pump, the bodyis blue and clean, the inlet SST filter is tan but not bad, cleaned with carb cleaner and reinstalled. Also cleaned filter on side of heater - clean too. Also checked tube feed into burner pot - clear.
Present situation with restrictor in place
1. On low burns 95% blue "acceptable" still some tinges of yellow intermittently
2. On Med 80% Blue with Yellow Tips
3. On High Yellow / some blue
4. On shutdown still fuming raw kero out of exhaust..
What do you experts say?
Bad solenoid pump, water in system? (I didnt drain the sump yet in the 422. since the filter port was clean - no water).
I dont beleive its air related as it burns cleaner slightly restricted so I am ruling out the blower motor at this point..
Thanks in advance..
Carl
It started shutting down last year, then this year every week or so it was shutting down so decided to have it rebuilt by Perfect Plumbing Lyman Me for $500 (kit was $300 so I felt the $200 investment wsa justified to be done by a pro who knows these units) I watched the entire process - new burner pot, ring all gaskets, cleaned and vacced the heat exchanger - lots of soot came out. Also replaced the oring on the damper assy as it was cracked, and filed down the tabs on the damper to prevent sticking. Also cleaned the small sump etc..
They checked the air flow with a manometer was low so they removed the restrictor donut and readings were acceptable (I think just under 2 on low and under 4 on high) It wasnt buring a nice blue flame so they came back again and checked the air and said this was the best they could do.. It would burn 90% blue 10% yellow on low, 75/25 blue/yellow on Med and 60/40 yellow/blue on high still not great..Also fume plumes from exhaust on shutdown.
Anyway three weeks after rebuild shut off again, restarted and it functioned until last week, -10 Mon AM, it was off again, so I tried to start and click-click - from reading here I decucted no fuel, so replaced the tank filter outside - it had 1/4" frozen gunk in base. While filter was off drained some kero - it was clear/red no water so installed the filter and bled the air out.
Now to the 422 click click a few times and alls good and running again, low, med and high, but flames still arent good. So on low I take off inlet air and play restrictor with my hand, and by reducing air its 95% blue on low! Great, so I put donut back in now 95% blue on low, with tinges of yellow at 10 and 2 oclock via the sight glass. On Med its 75% blue with yellow tips - still acceptable, on high mostly yellow with blue at the base. The damper is functioning properly as I can hear it click in/out as it cycles from high to lower.
Then on shutdown once the blower stops the exhaust fumes raw kerosene for 4-5 minutes.. not good as this is carboning up the HX I think..and also this points to solenoid pump not shutting down cutting off fuel I think maybe its dirty/got junk in it...
So today I removed solenoid pump, the bodyis blue and clean, the inlet SST filter is tan but not bad, cleaned with carb cleaner and reinstalled. Also cleaned filter on side of heater - clean too. Also checked tube feed into burner pot - clear.
Present situation with restrictor in place
1. On low burns 95% blue "acceptable" still some tinges of yellow intermittently
2. On Med 80% Blue with Yellow Tips
3. On High Yellow / some blue
4. On shutdown still fuming raw kero out of exhaust..
What do you experts say?
Bad solenoid pump, water in system? (I didnt drain the sump yet in the 422. since the filter port was clean - no water).
I dont beleive its air related as it burns cleaner slightly restricted so I am ruling out the blower motor at this point..
Thanks in advance..