First of all. when dealing with any existing pipe greater than 1" the 12" and 14" pipe wrenches are nearly useless. At a minimum I would have used an two 18" pipe wrench's and preferably an 18" to steady the fitting while turning the pipe with a 24" wrench, all the while keeping a 36" handy in case the 24" was difficult to turn.
Now that the 22.5deg elbow is loose, you have no alternative but to change it.Any time an NPT (National pipe taper) thread is reversed, no matter how slightly you must completely disconnect the joint, clean the threads, apply new PTFE tape or pipe dope, then reassemble the joint, however in this case you may not do that.
Back in the days when your drain & waste system was first put in cast iron (CI) pipe was state of the art however, even though there was 1-1/2 CI pipe available, as a rule they used CI pipe for lines 2" or greater and galvanized iron pipe (GIP), brass pipe, lead pipe or DWV grade copper pipe for 1-1/2" & 1-1/4" lines. in your case they used GIP. They did not make DWV or Sanitary grade fittings which have a short radius bend at all changes of direction therefore they used pressure fittings which have sharp angular bends. Once that 22.5deg fitting loosened you were committed to disconnect and redo that joint, however once the fitting is removed the act of replacing it is now defined as "new work" and you are obligated to meet the code standards that are in effect at the time the new work is performed, thus the 22.5deg elbow MUST BE replaced with a DWV grade 1/8th bend. Code also prohibits using any female threaded fittings therefore the only solution is to cut the pipe back, connect a short section of PVC to the existing GIP with a Fernco, then glue in a PVC 1/8th bend.
Code also now prohibits installing a Tee on a horizontal line therefore you should begin by cutting the horizontal line slightly downstream of that TEE and cut cut the vent line slightly above the TEE then tie in PVC to the drain line by means of a Fernco, install a wye & 1/8th bend or Combo at the vent location, tying the PVC into the vertical GIP vent by means of another Fernco and continue upstream to the tub location with new Schedule 40 PVC pipe.
Also, in reviewing the photos I could not help but notice that you do not have the proper hangers on the CPVC potable water distribution lines. Code requires all lines with the exception of PEX to have one hanger within 12" of any change of direction greater than 45deg and one hanger for every 48 linear inches of pipe. (PEX requires a hanger for every 36"). Code also prohibits using wire or metal hangers on plastic pipe, therefore you must install plastic J-hooks, plastic pipe hangers or plastic pipe strapping.
It should also be noted that when you install a PVC male adapter into a thread, you are required to apply 3 wraps of RED triple density PTFE Tape (Teflon tape*) or Thread Joint Compound to the threads prior to installing the fitting.
* The word "Teflon" is a proprietary trade name of Du Pont Corp, therefore the thread tape made by other manufacturers must be listed as PTFE, which is the chemical abbreviation for teflon.
Now that the 22.5deg elbow is loose, you have no alternative but to change it.Any time an NPT (National pipe taper) thread is reversed, no matter how slightly you must completely disconnect the joint, clean the threads, apply new PTFE tape or pipe dope, then reassemble the joint, however in this case you may not do that.
Back in the days when your drain & waste system was first put in cast iron (CI) pipe was state of the art however, even though there was 1-1/2 CI pipe available, as a rule they used CI pipe for lines 2" or greater and galvanized iron pipe (GIP), brass pipe, lead pipe or DWV grade copper pipe for 1-1/2" & 1-1/4" lines. in your case they used GIP. They did not make DWV or Sanitary grade fittings which have a short radius bend at all changes of direction therefore they used pressure fittings which have sharp angular bends. Once that 22.5deg fitting loosened you were committed to disconnect and redo that joint, however once the fitting is removed the act of replacing it is now defined as "new work" and you are obligated to meet the code standards that are in effect at the time the new work is performed, thus the 22.5deg elbow MUST BE replaced with a DWV grade 1/8th bend. Code also prohibits using any female threaded fittings therefore the only solution is to cut the pipe back, connect a short section of PVC to the existing GIP with a Fernco, then glue in a PVC 1/8th bend.
Code also now prohibits installing a Tee on a horizontal line therefore you should begin by cutting the horizontal line slightly downstream of that TEE and cut cut the vent line slightly above the TEE then tie in PVC to the drain line by means of a Fernco, install a wye & 1/8th bend or Combo at the vent location, tying the PVC into the vertical GIP vent by means of another Fernco and continue upstream to the tub location with new Schedule 40 PVC pipe.
Also, in reviewing the photos I could not help but notice that you do not have the proper hangers on the CPVC potable water distribution lines. Code requires all lines with the exception of PEX to have one hanger within 12" of any change of direction greater than 45deg and one hanger for every 48 linear inches of pipe. (PEX requires a hanger for every 36"). Code also prohibits using wire or metal hangers on plastic pipe, therefore you must install plastic J-hooks, plastic pipe hangers or plastic pipe strapping.
It should also be noted that when you install a PVC male adapter into a thread, you are required to apply 3 wraps of RED triple density PTFE Tape (Teflon tape*) or Thread Joint Compound to the threads prior to installing the fitting.
* The word "Teflon" is a proprietary trade name of Du Pont Corp, therefore the thread tape made by other manufacturers must be listed as PTFE, which is the chemical abbreviation for teflon.