  • pushkins
    General Contractor
    • Mar 2006
    • 1895

    #16
    Yes adding blocking and stapling to the blocking within 6-8" of the box will pass inspection.
    Little about a lot and a lot about a little.
    Every day is a learning day.

    Comment

    • HayZee518
      Deity
      • Jul 2004
      • 8747

      #17
      stapling to the face of the joist is no problem IF there is no chance of hitting the cable. the accepted practice is to install a nailer, like a piece of furring strip to the joist, then stapling the wire to the nailer. at least there is some support for the cable. drilling through the approx center of a joist is also permitted. hole diameter is about 5/8" or 3/4"

      Comment

      • Colonel
        New Member
        • Nov 2010
        • 20

        #18
        Thanks a million to both of you for your advice and time to help people on these forums out!!

        You will be seeing more of me around, unfortunately every ceiling tile I drop has a nightmare hidden behind it

        I am starting to wonder if there was ever any "legal" work done to anything in this house...

        see you soon