THHN Cable

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • hummas
    New Member
    • Aug 2004
    • 4

    #1

    THHN Cable

    Hi,
    Can THHN cable be ran inside a wall from a entry point from outside (using conduit) to a breakerbox about 3 ft away?

  • hummas
    New Member
    • Aug 2004
    • 4

    #2
    quote:Originally posted by hummas

    Hi,
    Can THHN cable be ran inside a wall from a entry point from outside (using conduit) to a breakerbox about 3 ft away?

    Comment

    • hummas
      New Member
      • Aug 2004
      • 4

      #3

      Hi,
      I think I have confused the question. Can you run THHN cable in walls between 2X4's without conduit? I cannot seem to find that answer in the NEC code book. Any help would be great.

      Comment

      • HayZee518
        Deity

        • Jul 2004
        • 8746

        #4
        THHN THWN is a single stranded conductor. It is available in a multitude of colors. It CANNOT be run by itself exposed within a wall or outside of the wall i.e. stapled to the studs, wallboard or other. It is meant to be installed in a suitable raceway - EMT, RIGID, PVC, WIREMOLD. Purpose of the raceway is to afford mechanical protection. Even if the wire is installed inside of the wall (technically) it is unprotected.

        Comment

        • hummas
          New Member
          • Aug 2004
          • 4

          #5
          Wow!
          Outstanding response time and worthy website.
          Thanks.
          I am so glad I registered.

          Thanks again.
          hummas

          Comment

          • LazyPup
            Deity

            • Apr 2004
            • 2316

            #6
            Hummas, Welcome aboard and glad we could be of assistance. We will look forward to seeing you often and ask that you tell your friends.