    Thanks again for your replies!
    I would certainly be very careful when opening both outlets and the breaker.
    I've opened a few outlets before, so I should be able to check for loose connections.
    I'm a bit doubtful to the broken outlet, only because the power was lost when a hairdryer was used simultaneously as a few other electrical devices using the same outlet. Sounds to me that it would be the time when a breaker would trip, but you are the experts.
    I would certainly shut off the main power when going in to any of these outlets...if no luck, I'll call the experts.
    Thanks again!
    • normel
      • Jul 2007
      • 30
      #17
      What usually happens is when a high current draw appliance is used (like a hairdryer) and there is a poor connection at a push-in, the resultant heating causes the connection to fail completely. Most of the time this is at a working receptacle and is usually the one closest to the failed ones.
      • froddan
        • Jun 2007
        • 28
        #18
        I got it!!! Thanks to you guys!
        Apparently, the outlet closest to the one where the hairdryer was plugged in had a loose connection, and I managed to fix it!
        Thanks a bunch to all of you who contributed to this! You guys were very helpful and perfectly correct in your advice!