    furnace go into lock out

    I have Snyder General gas fired-upflow furnace. It will lite but only run for seconds the fan never comes on. After several attemp it goes into lock out. I think it the fan & limit control or the gas valve control. Any help will be appreicated.

    Thanks.
  • HayZee518
    Deity

    • Jul 2004
    • 8746

    #2
    why do you think its the fan? the fan just circulates the hot air. I would be more inclined to check out the flame sense circuit for the main valve. check out the thermocouple which should be in the pilot flame.

    Comment

    • Riolenny
      New Member

      • Feb 2009
      • 16

      #3
      Thanks. I will look at the flame sensor.

      Comment

      • Riolenny
        New Member

        • Feb 2009
        • 16

        #4
        The new flame probe sensor worked. But now the fan will not kick on after the flame starts. I can turn the fan on cont. and it will come on just fine.
        Any ideas are welcomed.

        Thanks

        Comment

        • HayZee518
          Deity

          • Jul 2004
          • 8746

          #5
          the fan is controlled by an air plenum switch. basically it's a coil that is in the air stream and expands and rotates closing a set of contacts. the contacts can be set for minimum temp and a max temp band.

          Comment

          • Riolenny
            New Member

            • Feb 2009
            • 16

            #6
            HayZee thanks for all the help. Everything is works fine now.

            Thank again.