  • furnace go into lock out

    I have Snyder General gas fired-upflow furnace. It will lite but only run for seconds the fan never comes on. After several attemp it goes into lock out. I think it the fan & limit control or the gas valve control. Any help will be appreicated.

    Thanks.

  • #2
    why do you think its the fan? the fan just circulates the hot air. I would be more inclined to check out the flame sense circuit for the main valve. check out the thermocouple which should be in the pilot flame.

    Comment


    • #3
      Thanks. I will look at the flame sensor.

      Comment


      • #4
        The new flame probe sensor worked. But now the fan will not kick on after the flame starts. I can turn the fan on cont. and it will come on just fine.
        Any ideas are welcomed.

        Thanks

        Comment


        • #5
          the fan is controlled by an air plenum switch. basically it's a coil that is in the air stream and expands and rotates closing a set of contacts. the contacts can be set for minimum temp and a max temp band.

          Comment


          • #6
            HayZee thanks for all the help. Everything is works fine now.