This is directed towards Hawkins. I acquired a GF200 over the weekend. Would go through a purge and attempted ignition. Air switch was closed, combustion blower was running. After a time-out I got eight burner bars flashing. Point me in the right direction what to check, please!
Announcement
Collapse
No announcement yet.
Gf200
Collapse
Forum Top GA Ad Widget
Collapse
X
-
Gf 200
HayZee,
I do not have a GF 200 manual but I would think the values would be close to the GF 500 for the gas valves. The gas control valve P connector should be around 87 OHMs and the Gas Solenoid L should be 2400 OHMs. The M connector should be 2400 OHMs. The voltage for the gas valve L and M should be around 105 DC. The gas control valve should show 8.7Volts DC for one and 6.2 Volts DC on the other. If the voltages are not right the main board may be bad. Boards for Monitor have been expensive for a long time now.