Hi Redwood,
I went with the aav because there is no roof suitable to use nearby for venting since it has a downward pitch (inside ceiling follows pitch) plus there are windows nearby if I left the vent at the top. I wasn’t sure of any other options so in went with the aav. I know a neighbor is using one so I hope it is okay by code; will have to do some more homework.
(9pm) Brain storm...I was thinking that maybe I could run the vent pipe with the aav (with aav removed of course) into the wall and then along side the inside of the band joist and out the back and then make a right angle and connect to the new roof vent I plan to install. Can I run a vent pipe such a distance (15'+) and have various bends? I'll have to update the drawing so you can see what I am thinking.
Toilets:
There is about 12” (2x10 +) from top of drain pipe to bottom of floor. I’ll have to look up an upward rolled wye to see if it will fit and how the vent will connect so I can understand this layout.
So a wye has more of a smooth curve vs a sanitary tee and is better to use for turns when a ‘y’ is needed.
On the horizontal run I’ll use the 3x2x3 wye or the other option you have suggested.
As for the cleanouts, can I use a wye with a treaded cap?
Someone told me that a vented ‘y’ should flow towards the trap so the air flows smoothly…and if I understand you correctly…the vented ‘y’ should be installed no different than if water was coming down and therefore be installed so the flow is towards the sewer or down stream. Reverse of what I was told. My logic told me that was wrong because the water running down the pipe may hit the ‘y’ and start trying to go up and therefore slow the flow…I’m so glad you corrected that because now I can count on my logic again.
I think I understand what you mean by an upward pitch for the wye…that way waste can not back-flow into that part of the vent/drain. Is that correct?
Thanks once again,
DanLast edited by drgto; 01-30-2010, 08:05 PM.Comment
-
Hi Redwood,
I went with the aav because there is no roof suitable to use nearby for venting since it has a downward pitch (inside ceiling follows pitch) plus there are windows nearby if I left the vent at the top. I wasn’t sure of any other options so in went with the aav. I know a neighbor is using one so I hope it is okay by code; will have to do some more homework.
(9pm) Brain storm...I was thinking that maybe I could run the vent pipe with the aav (with aav removed of course) into the wall and then along side the inside of the band joist and out the back and then make a right angle and connect to the new roof vent I plan to install. Can I run a vent pipe such a distance (15'+) and have various bends? I'll have to update the drawing so you can see what I am thinking.
I can't see what you are doing but the code does specify distances to windows and other openings. This product may be of interest if you are doing any new vents through the roof. http://www.kozykollar.com/
Toilets:
There is about 12” (2x10 +) from top of drain pipe to bottom of floor. I’ll have to look up an upward rolled wye to see if it will fit and how the vent will connect so I can understand this layout.
So a wye has more of a smooth curve vs a sanitary tee and is better to use for turns when a ‘y’ is needed.
Yes it offers direction to the flow that is needed on the horizontal plane where the sani-tee is used vertical because of the gravity assist and also allowing air flow back along the top.
On the horizontal run I’ll use the 3x2x3 wye or the other option you have suggested.
As for the cleanouts, can I use a wye with a treaded cap?
Absolutely
Someone told me that a vented ‘y’ should flow towards the trap so the air flows smoothly…and if I understand you correctly…the vented ‘y’ should be installed no different than if water was coming down and therefore be installed so the flow is towards the sewer or down stream. Reverse of what I was told. My logic told me that was wrong because the water running down the pipe may hit the ‘y’ and start trying to go up and therefore slow the flow…I’m so glad you corrected that because now I can count on my logic again.
I think I understand what you mean by an upward pitch for the wye…that way waste can not back-flow into that part of the vent/drain. Is that correct?
Yes
Thanks once again,
Dan
I think you've got it pretty well now.I stayed at a Holiday Inn Express last night.
Now I can Plumb!
For great information on the history of sanitary sewers including the use of Redwood Pipe
Visit http://www.sewerhistory.org/
Did you know some Redwood Pipe is still in service today.Comment
-
Thank you!!
Thank you Redwood for all of your help, advise and providing me with the knowledge I needed to move forward.
I did have one more question. On the attached reviewed isometric drawing I removed the aav and made it so the vent will be connected to the new roof vent. However, I also changed the 3" pipe to 2" pipe for the washer drain and where the shower connected...is this OKAY is 3" pipe required?
DanComment
-
At the point where the washer drain connects to the shower and lav you should go up to 3" under many codes, it will help prevent the washer from coming up in the shower...
Also you should check the code requirements on sizing of the vent through the roof. I imagine in your area there is a requirement to upsize to prevent frost closure.I stayed at a Holiday Inn Express last night.