Hi - stumped by a thermostat or furnace problem
  • mike_001
    • Jan 2009
    I have a York G2FD series furnace run by Lux PSP511 thermostat. A couple of weeks ago the heating stopped working. I hit the reset button on the thermostat and that worked.
    The same thing happened twice more - every time, the furnace worked fine then failed to turn back on after a period of low temp settings. Now however the reset does not work anymore.
    I replaced the batteries on the thermostat, took the cover off - all wires seem clean and solidly attached.
    I'd really appreciate any suggestions.
    Thanks, mike
    I went to the lux site and copied something in the specs:
    NOT COMPATIBLE WITH:
     Multi-stage Heat Pumps
     Multi-stage Gas or Oil Furnaces
     3 Wire Hydronic Systems
    Is your system any of the above?
    • hvacwiz
      • Apr 2006
      • 97
      Take the cover of the t-stat back off, put a jumper between r-w if your furnace runs you more than likely need a new stat.
      • mike_001
        • Jan 2009
        I did it and you were right. bought a new thermostat and everything's fine!
        Much thanks, hvacwiz!
        mike
        • hvacwiz
          • Apr 2006
          • 97
          Your welcome.