Bryant 373LAV furnace with Code 31
  • skip
    • Dec 2010
    • 6
    The furnace in our attic is just not working and we are out of ideas. We have already replaced the pressure switch, and now it won't even run with us jumping the switch. Found a bird's nest in the vent up to the roof and removed that. (But it was never completely clogged. and that is an exhaust vent, isn't it? It runs to the inducer motor.) We've been advised to clear out the intake to the burner compartment, but can't figure out what or where that is. ANY help would be appreciated.
  • skip
    • Dec 2010
    • 6
    Still not working, any help would be great!
    I was also told to check the condensate discharge trap. But I think those are only on high-efficiency units?
    • hvactech126
      • Nov 2010
      • 42
      does the inducer run? Have you taken the flue pipe off the furnace to confirm you got everything out of the flue?
      It is what it is.......
      • skip
        • Dec 2010
        • 6
        The inducer runs. I took the flue pipe off and even tried running the furnace with the vent disconnected. Still didn't work.
        • hvactech126
          • Nov 2010
          • 42
          the port that the tube hooks to @ the inducer is probably plugged, try to clear it out with a paper clip or small drill bit. or i believe there is a vent blockage switch just above the p/s that may be tripped and cause that code because the orange wire goes through that switch either b4 or after the p/s
          • skip
            • Dec 2010
            • 6
            I have tried clearing out that port (another person i heard from called it a "nipple"), so I believe it is clear. I will check to try to find a vent blockage switch.
            • skip
              • Dec 2010
              • 6
              Making progress!!!!!!!!! But I still need help!
              I bypassed the vent blockage switch and got it to work! Now the question is do I just get a new switch, or can I "untrip" this one? There is a little tab sticking up from it that is very wiggly. Should it lock back into place? I pushed on it pretty hard and nothing happened.
              • hvactech126
                • Nov 2010
                • 42
                you should be able to reset it by pushing in on that tab between the wire terminals, if that does not work, then get a new one, however, I do not recommend running the furnace with any safety device bypassed! Glad you found the problem!
                • skip
                  • Dec 2010
                  • 6
                  So far, so good!!!!!!!!
                  Ok, this is the wife typing. It appears the switch was reset by pushing on it. It's working so far!!!!!!!!!!!!!!!!!!!!!!!!!!!!!!
                  And no, we would NEVER run it without all the safety things in place. We like living. (But it is always good to remind people about safety stuff.)