    Air pressure switch and transformers

    Is there any difference between using one off of a model 22 on a 41?

    thanks for any advice as they appear to be exchangeable.
  • hawkins111
    Master Journeyman

    • Mar 2010
    • 752

    #2
    Transformers are the same. Air Pressure switches are different. The switch for the M41 is much bigger and must trip at a different pressure. Tom

    Comment

    • msearcher
      Handyman

      • Mar 2011
      • 125

      #3
      Originally posted by hawkins111
      Transformers are the same. Air Pressure switches are different. The switch for the M41 is much bigger and must trip at a different pressure. Tom
      Thank you Tom, any way to tell a 422 from a 441 or a 22 from a 41 air pressure switch as they can look the same.

      Tom

      Comment

      • hawkins111
        Master Journeyman

        • Mar 2010
        • 752

        #4
        The M441 and M41 air pressure switch is much larger than the 21, 422. I believe the M441 and M41 are round where the M21 and 422 are square and much smaller. Tom

        Comment

        • msearcher
          Handyman

          • Mar 2011
          • 125

          #5
          Tom

          i have a 22 with the large round air switch like the 41 and also a 441's with both the large and later ones with the smaller square.

          tom

          Comment

          • hawkins111
            Master Journeyman

            • Mar 2010
            • 752

            #6
            The M22 with a large round air switch has an incorrect switch on it. Not saying it does not work, just that it is the wrong part. The M441 can have both a large and a small switch on it. I do not know when the change occurred. My M441 was made in 1996 and it has a small switch. The book has different part numbers for M22 and M41 , and M422 and M441. In all cases I have looked into when Monitor assigned a different part number, the part is different.

            Comment

            • msearcher
              Handyman

              • Mar 2011
              • 125

              #7
              Originally posted by hawkins111
              The M22 with a large round air switch has an incorrect switch on it. Not saying it does not work, just that it is the wrong part. The M441 can have both a large and a small switch on it. I do not know when the change occurred. My M441 was made in 1996 and it has a small switch. The book has different part numbers for M22 and M41 , and M422 and M441. In all cases I have looked into when Monitor assigned a different part number, the part is different.
              Thank you for your response.