Hi Guys,
I recently purchased a used Monitor 441 for use in my home. The unit was very clean and the installer commented that it appeared to have been used very little by the previous owner.
I do have a problem with the heater that I haven't been able to resolve.
When the heater is turned off for more than 3 hours and I go to use it, it will light and cycle on for several minutes, then shut off and the display will start blinking.
Through trial and error, I have found that if I turn the heater off, press the 'priming' button on the right hand side several times, then turn the heater back on, it will light and run properly. If I do not do this priming routine before turning the heater on for every use, it will not function for more than 2-3 minutes.
We have checked the internal fuel filter (clean) and fuel delivery is fine. Good fuel pressure. (I also have a Monitor 2400 upstairs that is working properly.)
Any ideas where to go from here?
Thanks!
**EDIT** --- MORE INFO:
After reading several of the threads on here, I wanted to go ahead and clarify a few things. Once I get the monitor started by doing the priming routine, it runs GREAT. Nice blue flame, etc. The heater even cycles on and off properly (after reaching desired temp). The problems only occurs when the heater has been turned off for 3+ hours.
I recently purchased a used Monitor 441 for use in my home. The unit was very clean and the installer commented that it appeared to have been used very little by the previous owner.
I do have a problem with the heater that I haven't been able to resolve.
When the heater is turned off for more than 3 hours and I go to use it, it will light and cycle on for several minutes, then shut off and the display will start blinking.
Through trial and error, I have found that if I turn the heater off, press the 'priming' button on the right hand side several times, then turn the heater back on, it will light and run properly. If I do not do this priming routine before turning the heater on for every use, it will not function for more than 2-3 minutes.
We have checked the internal fuel filter (clean) and fuel delivery is fine. Good fuel pressure. (I also have a Monitor 2400 upstairs that is working properly.)
Any ideas where to go from here?
Thanks!
**EDIT** --- MORE INFO:
After reading several of the threads on here, I wanted to go ahead and clarify a few things. Once I get the monitor started by doing the priming routine, it runs GREAT. Nice blue flame, etc. The heater even cycles on and off properly (after reaching desired temp). The problems only occurs when the heater has been turned off for 3+ hours.