    Blower will not shut off.

    The blower on my HVAC system continuously runs, even when I turn the system off. I have a Trane XE78 furnace with a White Rodgers 50A50-405 controller. Any ideas on what's wrong?
  • HayZee518
    Deity

    • Jul 2004
    • 8746

    #2
    see if the plenum hi limit switch is ON. there is a white button that is pulled out for continuous fan run. pushing the button IN allows for controlled operation.

    Comment

    • HayZee518
      Deity

      • Jul 2004
      • 8746

      #3
      The White Rodgers 50A50-405 control module is for heat only. It has a preset purge cycle for the burner, so it shouldn't affect the fan operation. Look into the circuit for fan operation. look on the print, it should tell you.

      Comment

      • LazyPup
        Deity

        • Apr 2004
        • 2316

        #4
        Check the fan relay to see if the NO(normally open) contacts are stuck in the NC(Normally closed) position.

        Comment

        • hvacwiz
          Handyman
          • Apr 2006
          • 97

          #5
          more than likely the fan reley is sticking on the furnace circuit board, if this is the case you will need to replace the entire board, the releys are not interchangeable

          Comment

          • Stumped
            New Member
            • Aug 2008
            • 2

            #6
            Thanks

            Thanks for the advice guys. Unfortunately the only available button of any type is the kill switch for when you take the cover off. Looks like I'll have to replace the White Rodgers control module after all. Yes the module is mainly for heat but it also controlls the fan when the system is set to ac.