hey, i have an old gas furnace, with a honeywell thermostat, the round design mechanical, not digital. the model number on it says CT 87A4471, i found a new one that is a different number: T87F2873, it looks the same. Is it basically the same one? Does anyone know if it will work?
question about Honeywell thermostats
Collapse
Forum Top GA Ad Widget
Collapse
X
-
Tags: None
-
The T872873 will work fine. You will have to check the amp draw at the thermostat and set the heat anticipator to match your reading.hey, i have an old gas furnace, with a honeywell thermostat, the round design mechanical, not digital. the model number on it says CT 87A4471, i found a new one that is a different number: T87F2873, it looks the same. Is it basically the same one? Does anyone know if it will work?
Checking this out will be different depending on if you have a millivolt, or a 24 volt gas valve. The T872873 is not made for a millivolt system, but it will work fine on a 24 volt system. The reason they did away with the stat is the mercury
switch. So don't let your kids eat the thermostat. Later PaulComment
-
thermostat question
thanks guys, one more question, i believe it's a 24 volt gas furnace, it's an old coleman gas furnace, it says 70,000 btu input and 49,000 output model # 2004C. Or, as my son says: it was made in the early 17th century. Anyhoo... won't any 24 V 2 wire heat only thermostat do the job??Comment
-
can't locate info on amp draw anywhere on heater, the old thermostat was like at 0 when I took it apart, how do you find the amp draw on this furnace? in order to set the anticipator on the new stat?Comment



Comment